manniste skrev:So as I beginning to understand, the blower values I kind a need to guess while looking at the flame.
But is there any settings that would help the boiler to lower the power by itself if reached its temperature. Right now it heats up and goes to Temp Stop, instead of just lowering the power. I mean is that normal and preferred? Its like takes too long for the burner to react when the temperature rises.
From your curves, it seems as if your pump run too slowly
and that the P value is too low.
Try a higher P.
perhaps 1.5
It would be a good idea if you put the link to your StokerCloud into the signature line.
So, it becomes easier to help