Baxi Multihead doesn't start after security shutdown

Indlæg af tomdk » 21 mar 2009 11:25

Hej,

undskyld jeg kan ikke taler dansk, herfra jeg skriver po engelsk.

I do have a problem with the heating system installed in my house. It is a Baxi Multihead although I do not know if it's a 1.5 or something else. After a security shutdown due to back burning along the conveying screw I can't restart the heating system.

I cleaned the pellet container and the burning cell, as well as the tube where the conveying screw is housed. So there is no tension on the conveying screw and everything is try. Since the fuse popped during the shutdown I would like to turn the system back on while activating the fuse again.

Every time I do this the fuse pops out almost immediately. Do you have any suggestions how to solve this problem?

Any fuses at the heating system to check or anything?

I appreciate all suggestions.

Thanks, Thomas


Brugeravatar
Jan_Al
Stoker X
Stoker X
Indlæg: 486
Tilmeldt: 09 okt 2008 19:54
Mit fyr: KSM 175-13
Areal: 154
Brændsel: Piller
Fremviser gerne i postnummer: 6430
Dagligt forbrug: ca. 20Kg.
Årligt forbrug: Sæson 09/10= 6,4T
Geografisk sted: Als, Sønderjylland
Givet likes: 16 gange
Modtaget likes: 7 gange

Re: Baxi Multihead doesn't start after security shutdown

Indlæg af Jan_Al » 21 mar 2009 12:11

There must be a dataplate on the unit somewhere. Try to locate it and write down the data here, then it will be a lot easyer to do some troubleshooting.

tomdk
Stoker I
Stoker I
Indlæg: 3
Tilmeldt: 21 mar 2009 11:03

Re: Baxi Multihead doesn't start after security shutdown

Indlæg af tomdk » 21 mar 2009 12:16

Yes, you are right. Found it and it is a Multihead 1.5
Any more details you need from this plate?

Thomas

Brugeravatar
Jan_Al
Stoker X
Stoker X
Indlæg: 486
Tilmeldt: 09 okt 2008 19:54
Mit fyr: KSM 175-13
Areal: 154
Brændsel: Piller
Fremviser gerne i postnummer: 6430
Dagligt forbrug: ca. 20Kg.
Årligt forbrug: Sæson 09/10= 6,4T
Geografisk sted: Als, Sønderjylland
Givet likes: 16 gange
Modtaget likes: 7 gange

Re: Baxi Multihead doesn't start after security shutdown

Indlæg af Jan_Al » 21 mar 2009 12:19

Is it the fuse in your house that pops or a circuit breaker trip in the unit?

tomdk
Stoker I
Stoker I
Indlæg: 3
Tilmeldt: 21 mar 2009 11:03

Re: Baxi Multihead doesn't start after security shutdown

Indlæg af tomdk » 21 mar 2009 12:23

When I turn the fuse in the house back on, the heating system response with a sound from the electronic and some mechanical sound and then the fuse in the house pops out again.

Thomas


Brugeravatar
Jan_Al
Stoker X
Stoker X
Indlæg: 486
Tilmeldt: 09 okt 2008 19:54
Mit fyr: KSM 175-13
Areal: 154
Brændsel: Piller
Fremviser gerne i postnummer: 6430
Dagligt forbrug: ca. 20Kg.
Årligt forbrug: Sæson 09/10= 6,4T
Geografisk sted: Als, Sønderjylland
Givet likes: 16 gange
Modtaget likes: 7 gange

Re: Baxi Multihead doesn't start after security shutdown

Indlæg af Jan_Al » 21 mar 2009 12:36

Try to locate the 2 contactors, K1 and K2, for the conveying screw. If the fuse blows when one of the contactors is activated, it is very likely that the motor of the conveying screw is faulty :(

Brugeravatar
thy
Supporter
Supporter
Indlæg: 10375
Tilmeldt: 09 dec 2006 17:17
Mit fyr: Baxi 1,5 350L
Areal: 190 +værksted 130
Brændsel: Estonia
Fremviser gerne i postnummer: 5560
Dagligt forbrug: ca 8-30
Årligt forbrug: ca 5-6
Geografisk sted: Frøbjerg (FYN)
Givet likes: 101 gange
Modtaget likes: 269 gange
Kontakt:

Re: Baxi Multihead doesn't start after security shutdown

Indlæg af thy » 21 mar 2009 16:51

hvor bor du..

try replace all 3 fuses... at the same time
Mvh thy.... ps viser gerne Banditten frem hvis det sku være 402.gif